Posted: 10/05/18 03:56pm Link  |  Quote  |  Print  |  Notify Moderator

I wanted a generator so I wouldn't have to run my 7000kw in the rv just to charge the batteries and run a few things.
Amazing what you can get for $250 these days

I have a Durastar 4400 generator but the hz would vary too much and it would trip error codes on my Progressive EMS and i couldn't just plug it into the rv since it would give a fault code on my inverter.

So I bought a dual fuel Sportsman
https://www.amazon.com/Sportsman-GEN4000........S-Sandstorm-4000-Generator/dp/B079RBD936http://www.amazon.com/Sportsman-GEN4000DF-SS-Sandstorm-4000-Generator/dp/B079RBD936

Works great on propane and the hz only varies from 61 to 62 hz
But the EMS shows an error code of open ground.
I even tried grounding the terminal lug into the ground and nothing changed
Everything works fine if I bypass the EMS

What else can I do to fix the open ground?

wnjj

Cornelius, Oregon

Senior Member

Joined: 01/11/2007

View Profile


Offline
Posted: 10/05/18 04:06pm Link  |  Quote  |  Print  |  Notify Moderator

185EZ wrote:

I wanted a generator so I wouldn't have to run my 7000kw in the rv just to charge the batteries and run a few things.
Amazing what you can get for $250 these days

I have a Durastar 4400 generator but the hz would vary too much and it would trip error codes on my Progressive EMS and i couldn't just plug it into the rv since it would give a fault code on my inverter.

So I bought a dual fuel Sportsman
https://www.amazon.com/Sportsman-GEN4000........S-Sandstorm-4000-Generator/dp/B079RBD936http://www.amazon.com/Sportsman-GEN4000DF-SS-Sandstorm-4000-Generator/dp/B079RBD936

Works great on propane and the hz only varies from 61 to 62 hz
But the EMS shows an error code of open ground.
I even tried grounding the terminal lug into the ground and nothing changed
Everything works fine if I bypass the EMS

What else can I do to fix the open ground?

You need to connect the ground pin to the neutral pin using a bonding plug at the generator or bypass your EMS when on generator power. You can probably bond one of the 20A outlets and it will suffice.

agesilaus

North Florida

Senior Member

Joined: 05/06/2008

View Profile



Good Sam RV Club Member

Offline
Posted: 10/05/18 04:16pm Link  |  Quote  |  Print  |  Notify Moderator

You may need to get an inverter genset that puts out true sine wave output. I cannot run my UPS, printer or several other bits of gear on my Champion 3500/4000 dual fuel non-inverter, but it works fine on my Champion 3500/4000 inverter. I doubt grounding it will correct the wave form. But I'm not an electrician or electrical engineer.


Arctic Fox 25Y Travel Trailer
2012 Ford F-350 4WD Lariat 6.7L
Straightline dual cam hitch
400W Solar with Victron controller
Superbumper


185EZ

Lake Havasu City, AZ

Full Member

Joined: 09/28/2018

View Profile



Posted: 10/05/18 04:34pm Link  |  Quote  |  Print  |  Notify Moderator

wnjj wrote:

185EZ wrote:

I wanted a generator so I wouldn't have to run my 7000kw in the rv just to charge the batteries and run a few things.
Amazing what you can get for $250 these days

I have a Durastar 4400 generator but the hz would vary too much and it would trip error codes on my Progressive EMS and i couldn't just plug it into the rv since it would give a fault code on my inverter.

So I bought a dual fuel Sportsman
https://www.amazon.com/Sportsman-GEN4000........S-Sandstorm-4000-Generator/dp/B079RBD936http://www.amazon.com/Sportsman-GEN4000DF-SS-Sandstorm-4000-Generator/dp/B079RBD936

Works great on propane and the hz only varies from 61 to 62 hz
But the EMS shows an error code of open ground.
I even tried grounding the terminal lug into the ground and nothing changed
Everything works fine if I bypass the EMS

What else can I do to fix the open ground?

You need to connect the ground pin to the neutral pin using a bonding plug at the generator or bypass your EMS when on generator power. You can probably bond one of the 20A outlets and it will suffice.

I know enough to get by but I have no idea what you just said lol
I'm fine knowing the EMS is within range and unplugging it to use the generator.
Is the open ground anything to really be worried about?
I don't want to be connecting pins and bonding things at this time unless it isn't a big deal.
appreciate the help.

Teamfour

Sterling, VA

Senior Member

Joined: 03/03/2004

View Profile



Good Sam RV Club Member


Posted: 10/05/18 04:46pm Link  |  Quote  |  Print  |  Notify Moderator

Yep, you just need a bonding plug. I made my own ($4) to get rid of the E2 code on the EMS. Here's one already made if you don't want to try it yourself.

Bonding plug


Lee and Anne


2016 F250 2WD CC SB XLT 6.2 3.73 locker, 3,295 Payload
2014 Salem Hemisphere 282RK 7.8k lbs loaded, Equal-i-zer WDH


road-runner

Oregon

Senior Member

Joined: 05/03/2015

View Profile


Offline
Posted: 10/05/18 04:56pm Link  |  Quote  |  Print  |  Notify Moderator

The "open ground" diagnosis is not correct. It's the most likely guess by the EMS based on what it can discern from the two hot wires plus the safety ground wire. When you're on shore power the open ground diagnosis has a high probability of being correct. When being powered by an unbonded generator, it's an incorrect diagnosis. Shore power has what's called a "neutral-ground bond", where the neutral conductor and ground conductor are connected upstream of the power output. The majority of portable generators do not have this neutral-ground bond, and the EMS wrongly diagnoses it as an open ground. To make the EMS happy you need to add this neutral-ground bond. Many people think the simplest way is to take a standard plug and wire the neutral (wide blade) and ground pins together, then plug it into the same generator outlet that you plug the RV into. There have been pictures posted, but with the forum requiring pictures to be hosted on an outside web site, all the ones I know about are gone. Take a look here for more info: http://noshockzone.org/generator-ground-neutral-bonding/ . To read more, search for "generator bonding plug" and you'll find lots to read, videos, and even pre-made ones to purchase.


2009 Fleetwood Icon

Teamfour

Sterling, VA

Senior Member

Joined: 03/03/2004

View Profile



Good Sam RV Club Member


Posted: 10/05/18 05:13pm Link  |  Quote  |  Print  |  Notify Moderator

road-runner wrote:

The "open ground" diagnosis is not correct.


The open ground diagnosis is correct. Straight from the folks who make the EMS:
Open Ground Protection:

If AC power has an open ground condition, the EMS will read an error code of E-2 and power will not be allowed to the RV.

agesilaus

North Florida

Senior Member

Joined: 05/06/2008

View Profile



Good Sam RV Club Member

Offline
Posted: 10/05/18 05:24pm Link  |  Quote  |  Print  |  Notify Moderator

The bonding plug idea is interesting, I'll be trying that asap.

enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile






Posted: 10/05/18 05:34pm Link  |  Quote  |  Print  |  Notify Moderator

You can buy a standard three wire cord body. Open it up as to install a cord. Get a short piece of 12 or 14 gauge wire, about two inches will be plenty. Strip the wire ends about 1/2 inch. Connect one end to the green screw, connect the other end to the silver screw. Re-assemble. Plug it into one of the receptacle on the genset.
That is all there is to do.


Bud
USAF Retired
Pace Arrow

2003 Chev Ice Road Tracker


185EZ

Lake Havasu City, AZ

Full Member

Joined: 09/28/2018

View Profile



Posted: 10/05/18 05:38pm Link  |  Quote  |  Print  |  Notify Moderator

You guys are awesome!
Thanks for the help.[emoticon]
I thought i was going to have to return a generator

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 6  
Next

Open Roads Forum  >  Tech Issues

 > Portable Generator open ground
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2018 CWI, Inc. © 2018 Good Sam Enterprises, LLC. All Rights Reserved. | Terms of Use | PRIVACY POLICY | YOUR PRIVACY RIGHTS