Might also check and be sure there is not another GFCI on the same circuit which is tripped

ScottG

Bothell Wa.

Senior Member

Joined: 02/25/2005

View Profile


Offline
Posted: 01/22/20 08:02pm Link  |  Quote  |  Print  |  Notify Moderator

For some strange reason, the manufacturers of GFCI swapped the "line" and "load" connections from top to bottom a few years back. So if you hook up the new one exaclty the same as an old one, it would be backwards and dead. Might verify the connections.


Scott, Grace and Wesly
2003 Dodge 3500 4x4, 6 speed Cummins.
2018 Silver Fox 32A.
H0NDA eu2000i

ktmrfs

Portland, Oregon

Senior Member

Joined: 06/22/2005

View Profile


Offline
Posted: 01/22/20 08:44pm Link  |  Quote  |  Print  |  Notify Moderator

DrewE wrote:

You have power in as much as the lights on the GFCI are illuminating.

A new GFCI wouldn't reset for three possible reasons, provided it does have power:
1. You have a ground fault of some sort downstream. A bit of water in the outdoor outlet would be one quite believable cause for this.
2. You have the line and load connections mixed up (on some models, not all).
3. Very rarely, you got a broken unit from the factory.


add (4) ground and neutral shorted downstream of the GFCI. This will also trip a GFCI.


2011 Keystone Outback 295RE
2004 14' bikehauler with full living quarters
2015.5 Denali 4x4 CC/SB Duramax/Allison
2004.5 Silverado 4x4 CC/SB Duramax/Allison passed on to our Son!


DrewE

Vermont

Senior Member

Joined: 08/23/2014

View Profile


Offline
Posted: 01/22/20 09:06pm Link  |  Quote  |  Print  |  Notify Moderator

ktmrfs wrote:

DrewE wrote:

You have power in as much as the lights on the GFCI are illuminating.

A new GFCI wouldn't reset for three possible reasons, provided it does have power:
1. You have a ground fault of some sort downstream. A bit of water in the outdoor outlet would be one quite believable cause for this.
2. You have the line and load connections mixed up (on some models, not all).
3. Very rarely, you got a broken unit from the factory.


add (4) ground and neutral shorted downstream of the GFCI. This will also trip a GFCI.


That is true. I was considering that to be a form of ground fault, but it's good to call it out separately. It's also not too uncommon to find, particularly when putting in a GFCI where one was not previously there, since such shorts can easily go undetected and don't in themselves cause any problems in an otherwise properly constructed and working electrical system.





DFord

Near St Louis, MO

Senior Member

Joined: 12/16/2001

View Profile





Offline
Posted: 01/22/20 09:27pm Link  |  Quote  |  Print  |  Notify Moderator

The receptacle behind the refrigerator accessible through the outside refrigerator panel on our MH is also connected to our GFCI. Be sure to check it.


Don Ford
2004 Safari Trek 31SBD (F53/V10 20,500GVW)
'09 HHR 2LT or '97 Aerostar MiniVan (Remco driveshaft disconnect) for Towed vehicles
BlueOx Aventa II Towbar - ReadyBrake Inertia Brake System


time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 01/22/20 10:19pm Link  |  Quote  |  Print  |  Notify Moderator

ENG2242 wrote:

We have had a tremendous amount of rain here, am I correct in assuming that the outlet that is located outside and had a cord plugged into it when it was raining may be the culprit? If not please advise. Thanks so much, David
Yes a damp exterior outlet can allow leakage to ground and trip the GFCI. If you have an air compressor you could try to dry it out some.


2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675w Solar pictures back up

wa8yxm

Wherever I happen to park

Senior Member

Joined: 07/04/2006

View Profile


Offline
Posted: 01/23/20 07:05am Link  |  Quote  |  Print  |  Notify Moderator

The constant green light suggests it's already "Set" but the flickering red suggests a screw loose.. Many RVers have a few screws loose.. Most take a #2 Square bit (or #2 Phillips) and many can be found in the area of the circuit breakers.. Be sure to unplug before you TIGHTEN EVERY SCREW IN THAT BOX.


Home is where I park it.
Kenwood TS-2000 housed in a 2005 Damon Intruder 377


Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 2  
Prev

Open Roads Forum  >  Tech Issues

 > New GFI Outlet Will Not Reset
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2020 CWI, Inc. © 2020 Good Sam Enterprises, LLC. All Rights Reserved.