2ACs per rig has to get really close to averaging out to 4kw per site, 75% load factor on the transformer is a bit too close for my blood, especially since there's going to be other loads like water heaters, refrigerators, microwaves, etc. I mean since you get murdered on peak usage as a commercial user I can kinda understand why the park wouldn't want too much capacity, but pushing the equipment that hard is why we run into these undervoltage conditions.


2017 KZ Sportsmen Classic 181BH
2015 GMC 1500 Sierra 4x4 5.3 3.42 long bed
E2 WDH


wanderingaimlessly

SOBOVA

Senior Member

Joined: 08/23/2017

View Profile


Offline
Posted: 07/04/20 05:31am Link  |  Quote  |  Print  |  Notify Moderator

time2roll wrote:

wanderingaimlessly wrote:

time2roll wrote:

wanderingaimlessly wrote:


Do you really think they will go out at midnight to connect?
They will start connecting as soon as they arrive and then complain that their AC isn't working, anything but admit it's their own doing.
Car has a timer. Will be sound asleep.

They will want to do things and go places, and the 120 volt is slow, so they will be starting asap in most cases.
It takes 4 days on a Tesla S to fully recharge.
tesla charge

and you know the trucks will have even larger banksn needing even more time.

* This post was edited 07/04/20 06:05am by wanderingaimlessly *

valhalla360

No paticular place.

Senior Member

Joined: 08/19/2009

View Profile



Posted: 07/04/20 06:07am Link  |  Quote  |  Print  |  Notify Moderator

CA Traveler wrote:

Actually, the NEC code allows for derating factor and that is common. And the panels main CB would trip to provide protection from overloading and fire.


The answer is in the middle...yes, they do allow derating on the assumption that not every pedestal would be at peak power demand.

It's not a 50% derating.

Also, 30amps is a nominal rating for the outlet Your average air/con only pulls 10-12amps. Add in 3-5amps for fridge and other light loads, and the average rig is drawing less than 17amps, so if voltage is dropping significantly, that implies an inadequate electrical system.


Tammy & Mike
Ford F250 V10
2008 Copper Canyon 5er
Catalac Catamaran 34'
Full Time spliting time between boat and 5er


time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 07/04/20 08:47am Link  |  Quote  |  Print  |  Notify Moderator

afidel wrote:

2ACs per rig has to get really close to averaging out to 4kw per site, 75% load factor on the transformer is a bit too close for my blood, especially since there's going to be other loads like water heaters, refrigerators, microwaves, etc. I mean since you get murdered on peak usage as a commercial user I can kinda understand why the park wouldn't want too much capacity, but pushing the equipment that hard is why we run into these undervoltage conditions.
50 amp is 12,000 watts. 4kW is closer to 33%.


2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675w Solar pictures back up

time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 07/04/20 08:51am Link  |  Quote  |  Print  |  Notify Moderator

valhalla360 wrote:

CA Traveler wrote:

Actually, the NEC code allows for derating factor and that is common. And the panels main CB would trip to provide protection from overloading and fire.


The answer is in the middle...yes, they do allow derating on the assumption that not every pedestal would be at peak power demand.

It's not a 50% derating.

Also, 30amps is a nominal rating for the outlet Your average air/con only pulls 10-12amps. Add in 3-5amps for fridge and other light loads, and the average rig is drawing less than 17amps, so if voltage is dropping significantly, that implies an inadequate electrical system.
You are correct it is not 50%.... because it is as low as 41%

See table 551.73

http://www.electrician2.com/tables/Table551_73.pdf

CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile


Online
Posted: 07/04/20 09:44am Link  |  Quote  |  Print  |  Notify Moderator

Derating generally works simply because all of the pedestals are not at the maximum loads. However, todays rigs generally use more AC power and every summer there are posts about low voltage or tripping CBs. Especially for 30A pedestals.

In 2004 I had a 50A MH and there were limited 50A pedestals available. Upgrades are expensive but the demand has significantly increased availability of 50A since that time.


2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob


CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile


Online
Posted: 07/04/20 10:17am Link  |  Quote  |  Print  |  Notify Moderator

Consider many 30A (3600W) rigs built (still are?) with 2 ACs and contain a device that does not allow both AC's to run simultaneously because owners don't understand and want tripped CBs. Many of those same rigs had 5600W gens that could easily power 2 A/Cs along with other loads.

CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile


Online
Posted: 07/04/20 10:27am Link  |  Quote  |  Print  |  Notify Moderator

I visit a park that was 30A only. They recently upgraded about half of the sites to 50A. Why not all sites as it was largely a DIY and donation project? The answer was cost. The utility power panel would have to upgrade the incoming power and distribution center and that cost could not be justified.

TurnThePage

North ID

Senior Member

Joined: 10/08/2003

View Profile


Offline
Posted: 07/04/20 10:36am Link  |  Quote  |  Print  |  Notify Moderator

Good job on the OP for figuring out how to make it work. In the meantime, I just looked at the Hughes Autoformer. It says it may not be compatible with pedestals with GFCI. That sounds a little ominous...


2015 Ram 1500
2004 Pioneer 18T6

CavemanCharlie

Storden,MN

Senior Member

Joined: 03/01/2012

View Profile


Offline
Posted: 07/05/20 11:47am Link  |  Quote  |  Print  |  Notify Moderator

Lynnmor wrote:

The voltage will be the same at both the 50 & 30 amp receptacles.


No Not Always. I've tried it out.

It could be because the 30 amp plug gets more use and is more wore out but, I know of one park in particular that I always have to use the 50 amp plug to get the voltage high enough to make me feel more comfortable.

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 4  
Prev  |  Next

Open Roads Forum  >  Travel Trailers  >  General Q&A

 > marginal park power on hot days
Search:   Advanced Search

Search only in Travel Trailers


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2020 CWI, Inc. © 2020 Good Sam Enterprises, LLC. All Rights Reserved.