Posted: 01/04/22 05:10pm Link  |  Quote  |  Print  |  Notify Moderator

I have a 1300W microwave (120v) I’m trying to run using my Champion C46540 but the microwave shuts down about 5 to 10 seconds after I turn it on.

I know the generator isn’t overloaded running other stuff. It is lightly loaded running a few led and cfl lightbulbs. It runs a fridge and more lights and coffee maker just fine, although was not running any of these when the microwave kept shutting down.

I’m using the 4-prong 30R receptacle to power the breaker panel. At only 1300W the microwave should run just fine. What’s going on?

* This post was edited 01/04/22 07:52pm by tonyclifton *

KD4UPL

Swoope, VA

Senior Member

Joined: 03/16/2008

View Profile



Good Sam RV Club Member

Offline
Posted: 01/04/22 05:25pm Link  |  Quote  |  Print  |  Notify Moderator

I would suspect a the generator is slowing too much and the frequency is dropping too far below 60 Hz. It could also be dropping the voltage too much. Have you measured the frequency or voltage when it's running? I'd compare it to when it's running the coffee maker as that should be similar sized load. Coffee makers probably don't care much about voltage or frequency.
Keep in mind too, if your microwave is rated at 1,300 watts that's usually it's "cooking power". It's actual power draw from the generator will be a couple hundred watts more. That's not enough to make a difference unless you're running other loads at the same time maybe.

2112

Texas

Senior Member

Joined: 07/16/2011

View Profile



Posted: 01/04/22 06:07pm Link  |  Quote  |  Print  |  Notify Moderator

That's an old generator. The generator total harmonic distortion (THD) many be too high or the output voltage may be too low. If may be time to replace the brushes.

Does the microwave have a loud hum when running?


2011 Ford F-150 EcoBoost SuperCab Max Tow, 2084# Payload, 11,300# Tow,
Timbrens, PullRite SuperGlide 2700 15K
2013 KZ Durango 2857


Skibane

San Antonio, TX

Senior Member

Joined: 11/09/2005

View Profile


Offline
Posted: 01/04/22 06:08pm Link  |  Quote  |  Print  |  Notify Moderator

That model is rated for 3.5 KW continuous, and has an automatic voltage regulator circuit - so it should be capable of powering just about any microwave oven.

Microwaves aren't particularly picky about the AC line frequency, so it should still work even if the frequency is a few Hz off.

You might try measuring the AC voltage at the same receptacle the microwave is plugged in to - while the microwave is running. Look for excessive voltage drop as soon as the microwave is turned on.

* This post was edited 01/04/22 06:24pm by Skibane *

enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile






Posted: 01/04/22 06:16pm Link  |  Quote  |  Print  |  Notify Moderator

OP: What you posted for connection is not correct. The four pin twist lock is a 120/240 genset output. The 30TT three wire receptacle is 120 volt.
The twist lock only has a 240 volt output rated at 14.6 amps. See page 6 of owner's manual
You should be using the 30TT recptacle to get full load from genset.
What is shore power connection in your rig?

* This post was edited 01/04/22 07:16pm by enblethen *


Bud
USAF Retired
Pace Arrow

2003 Chev Ice Road Tracker


wnjj

Cornelius, Oregon

Senior Member

Joined: 01/11/2007

View Profile


Offline
Posted: 01/04/22 06:59pm Link  |  Quote  |  Print  |  Notify Moderator

enblethen wrote:

OP: What you posted for connection is not correct. The hour pin twist lock is a 120/240 genset output. The 30TT three wire receptacle is 120 volt.
The twist lock only has a 240 volt output rated at 14.6 amps. See page 6 of owner's manual
You should be using the 30TT recptacle to get full load from genset.
What is shore power connection in your rig?

This makes sense. If you are indeed using the 4 pin connector to a 50A 4 pin RV cord you are only able to use 1/2 of that power for any one of the 120V devices.

Our 2000W Honda struggles with the microwave so 1/2 of 3500W would definitely do so.

Since your RV doesn't need 240V, using the 30TT will allow all of the wattage at 120V, which in turn can be connected to both legs of the RV via an adapter.

enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile






Posted: 01/04/22 07:12pm Link  |  Quote  |  Print  |  Notify Moderator

I better clarify that the twist lock is 120/240 four wire. 14.6 amps total, indicating it would be somewhere around 7 amps per 120 leg.

jkwilson

Indiana

Senior Member

Joined: 06/14/2010

View Profile


Offline
Posted: 01/04/22 07:15pm Link  |  Quote  |  Print  |  Notify Moderator

In addition to the output of the generator, you need to consider that microwave power ratings are output power. A 1300W microwave may use 2000W from the power source.


John & Kathy
2014 Grand Design Reflection 303RLS
2014 F250 SBCC 6.2L 3.73

2112

Texas

Senior Member

Joined: 07/16/2011

View Profile



Posted: 01/04/22 07:30pm Link  |  Quote  |  Print  |  Notify Moderator

Also consider many split single phase generators have the AVR on only 1 phase. If you are loading up the non regulated side the voltage would certainly drop.

valhalla360

No paticular place.

Senior Member

Joined: 08/19/2009

View Profile



Good Sam RV Club Member


Posted: 01/04/22 07:38pm Link  |  Quote  |  Print  |  Notify Moderator

If the battery charger or hot water heater kicking on? Add that to lights, fridge and a few other minor loads and you could be overloading it...but I would expect a breaker to pop rather than the microwave to stop on it's own.

As mentioned, put a meter on the outlet adjacent to the microwave plug to see if you can see any voltage/hz issues. If you have a kill-o-watt device, put that in-line to see what the wattage draw looks like.


Tammy & Mike
Ford F250 V10
2021 Gray Wolf
Gemini Catamaran 34'
Full Time spliting time between boat and RV


Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 5  
Next

Open Roads Forum  >  Tech Issues

 > Why won’t my Champion C46540 generator run the microwave?
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2022 CWI, Inc. © 2022 Good Sam Enterprises, LLC. All Rights Reserved.